manuals.online logo
Brands
  1. Home
  2. •
  3. Brands
  4. •
  5. IDEAL
  6. •
  7. Boiler
  8. •
  9. IDEAL F400 User manual

IDEAL F400 User manual

This manual suits for next models

3

Other IDEAL Boiler manuals

IDEAL MINI C24 User manual

IDEAL

IDEAL MINI C24 User manual

IDEAL Vogue Combi c26 User manual

IDEAL

IDEAL Vogue Combi c26 User manual

IDEAL he15 User manual

IDEAL

IDEAL he15 User manual

IDEAL m30100 User guide

IDEAL

IDEAL m30100 User guide

IDEAL Classic SE9 RS User manual

IDEAL

IDEAL Classic SE9 RS User manual

IDEAL LOGIC+ SYSTEM2 S15 User guide

IDEAL

IDEAL LOGIC+ SYSTEM2 S15 User guide

IDEAL COMBI ESP 24 User manual

IDEAL

IDEAL COMBI ESP 24 User manual

IDEAL Classic SE9 FF User guide

IDEAL

IDEAL Classic SE9 FF User guide

IDEAL he15 User manual

IDEAL

IDEAL he15 User manual

IDEAL Falcon GTS 4 User manual

IDEAL

IDEAL Falcon GTS 4 User manual

IDEAL he15 User manual

IDEAL

IDEAL he15 User manual

IDEAL Exalt FSB 110 User guide

IDEAL

IDEAL Exalt FSB 110 User guide

IDEAL EVO S 50 User manual

IDEAL

IDEAL EVO S 50 User manual

IDEAL INSTINCT 40 User manual

IDEAL

IDEAL INSTINCT 40 User manual

IDEAL Concord CXS 40 User guide

IDEAL

IDEAL Concord CXS 40 User guide

IDEAL Vogue Combi c26 User manual

IDEAL

IDEAL Vogue Combi c26 User manual

IDEAL RS 50 Installation instructions

IDEAL

IDEAL RS 50 Installation instructions

IDEAL Henrad SEC 80FF User guide

IDEAL

IDEAL Henrad SEC 80FF User guide

IDEAL British Gas 100 RD2 Datasheet

IDEAL

IDEAL British Gas 100 RD2 Datasheet

IDEAL Response FF80 User manual

IDEAL

IDEAL Response FF80 User manual

IDEAL CONCORD SUPER SERIES 4 User manual

IDEAL

IDEAL CONCORD SUPER SERIES 4 User manual

IDEAL classic FF 250 User manual

IDEAL

IDEAL classic FF 250 User manual

IDEAL Vogue S15 User manual

IDEAL

IDEAL Vogue S15 User manual

IDEAL Logic+ SYSTEM 15 User manual

IDEAL

IDEAL Logic+ SYSTEM 15 User manual

Popular Boiler manuals by other brands

UTICA BOILERS BC3D Installation, operation & maintenance manual

UTICA BOILERS

UTICA BOILERS BC3D Installation, operation & maintenance manual

Lochinvar SOLUTION 260000 Installation & service manual

Lochinvar

Lochinvar SOLUTION 260000 Installation & service manual

Weil-McLain EG 6 Series manual

Weil-McLain

Weil-McLain EG 6 Series manual

RBI LCD Series Installation & operation manual

RBI

RBI LCD Series Installation & operation manual

Baxi MainEco Combi 28 Installation and service manual

Baxi

Baxi MainEco Combi 28 Installation and service manual

Unical ALKON R 24 Installation and Servicing Manual

Unical

Unical ALKON R 24 Installation and Servicing Manual

Automatic Heating Gasogen Installation and Servicing Manual

Automatic Heating

Automatic Heating Gasogen Installation and Servicing Manual

Viessmann VITORADIAL 300-T Type VR3 Service instructions for contractors

Viessmann

Viessmann VITORADIAL 300-T Type VR3 Service instructions for contractors

Alpha GasSaver GS-1 Installation and servicing instructions

Alpha

Alpha GasSaver GS-1 Installation and servicing instructions

Baxi ROCA LAURA PLUS 28/28 Operating, cleaning and maintenance instructions for the user

Baxi

Baxi ROCA LAURA PLUS 28/28 Operating, cleaning and maintenance instructions for the user

Vaillant uniSTOR VIH SW GB 500 BES operating instructions

Vaillant

Vaillant uniSTOR VIH SW GB 500 BES operating instructions

Kärcher HWE 4000 Gas manual

Kärcher

Kärcher HWE 4000 Gas manual

Radijator BIO max 23.1 instruction manual

Radijator

Radijator BIO max 23.1 instruction manual

Granby BKC Installation, operation and maintenance manual

Granby

Granby BKC Installation, operation and maintenance manual

Brunner BSV 20 Instructions for use

Brunner

Brunner BSV 20 Instructions for use

Potterton 50e Installation and Servicing Manual

Potterton

Potterton 50e Installation and Servicing Manual

UTICA BOILERS TriFire Assembly instructions

UTICA BOILERS

UTICA BOILERS TriFire Assembly instructions

ECR International UB90-125 Installation, operation & maintenance manual

ECR International

ECR International UB90-125 Installation, operation & maintenance manual

manuals.online logo
manuals.online logoBrands
  • About & Mission
  • Contact us
  • Privacy Policy
  • Terms and Conditions

Copyright 2025 Manuals.Online. All Rights Reserved.

installation and
servicing
Your Ideal installation and servicing guide
See reverse for users guide
When replacing any part on this appliance, use only spare parts that you can be
assured conform to the safety and performance specification that we require. Do not
use reconditioned or copy parts that have not been clearly authorised by Ideal Boilers.
xtra
Models F320, F400, F480, F560
xtra
February 2010 UIN 202863 A06
2
xtra
- Installation & Servicing
GENERAL
CAUTION.
To avoid the possibility of injury during the installation, servicing or cleaning
of this appliance, care should be taken when handling edges of sheet steel components.
Table 1 Performance Data
Boiler F320 F400 F480 F560
Boiler output Max kW 311.6 390.8 469.0 547.2
(non-condensing) Btu/h 1,063,200 1,333,400 1,600,200 1,867,000
Mean 70oC Min kW 67.8 97.7 105.5 107.7
Btu/h 231,300 333,400 360,000 367,500
Boiler output Max kW 329.0 415.6 498.8 581.8
(condensing) Btu/h 1,122,500 1,418,000 1,701,900 1,985,100
Mean 40oC Min kW 75.3 107.5 116.1 118.3
Btu/h 256,900 366,800 396,100 403,600
Boiler Input Net kW 320 400 480 560
Max Rate Btu/h 1,091,800 1,364,800 1,637,800 1,910,700
Gross kW 355.4 444.2 533.0 621.8
Btu/h 1,212,600 1,515,600 1,818,600 2,121,600
Boiler Input Net kW 70 100 108 110
Min Rate Btu/h 238,800 341,200 368,500 375,300
Gross kW 77.6 110.9 119.8 122.0
Btu/h 264,800 378,400 408,800 416,300
Maximum Gas Rate m3/h 32.2 40.2 48.4 56.4
ft3/h 1138 1420 1710 1992
Approx. flue gas @ max. rate m3/h 484 604 726 846
volume (@80oC) i.e. non-condensing ft3/h 17,100 21,380 25,640 29,920
Max. Flue Resistance Pa 145 145 145 145
Flue Gas CO2@ Max Rate % 9.3/9.8 9.3/9.8 9.3/9.8 9.3/9.8
G20/LNG @ Min. Rate % 9.1/9.6 9.1/9.6 9.1/9.6 9.1/9.6
NOx with O2= 0% mg/kWh 35 26 26 26
ppm 20 15 15 15
Seasonal Boiler Efficiency (Building Regs L2) 95.1 95.2 95.2 95.2
Note.
Natural gas consumption is calculated using a calorific value of
37.8MJ/m3(1038Btu/ft3) gross or 34 MJ/m3(910 Btu/ft3) nett at
15oC and 1013.25 mbar.
a. For l/s divide the gross heat input (kW) by the gross C.V. of
the gas (MJ/m3)
b. For ft/h3divide the gross heat input (Btu/h) by the gross C.V.
of the gas (Btu/ft3).
HEALTH & SAFETY DOCUMENT NO. 635
The electricity at work regulations, 1989. The manufacturer's
notes must NOT be taken, in any way, as overriding statutory
obligations.
IMPORTANT. These appliances are CE certified for safety and
performance. It is, therefore, important that no external control
devices, e.g. flue dampers, economisers etc., are directly
connected to these appliances unless covered by these
Installation and Servicing Instructions or as otherwise
recommended by Ideal Stelrad Group in writing. If in doubt
please enquire.
Any direct connection of a control device not approved by Ideal
Stelrad Group could invalidate the certification and the normal
appliance warranty. It could also infringe the Gas Safety
Regulations and the above regulations.
Electricity supply and Fuse rating for pumps etc. refer to manufacturer's instructions.
* OPTIONAL HEADER PACK HAS DN80 CONNECTIONS FOR FLOW AND RETURN AND 2" BSP GAS CONNECTION
Table 2 General Data
Boiler F320 F400 F480 F560
Gas supply 2H - G20 - 20mbar
Gas supply connection (in. BSP) 2 x R1 2 x R1 2 x R1 2 x R1
Flow connection (in. BSP) 2 x R2 2 x R2 2 x R2 2 x R2
Return connection (in. BSP) 2 x R2 2 x R2 2 x R2 2 x R2
Hydraulic Resistance @ 20oC mbar 100 105 110 120
Max Press (sealed system) bar (psi) 6 (87) 6 (87) 6 (87) 6 (87)
Maximum Static Head m (ft) 61 (200) 61 (200) 61 (200) 61 (200)
Boiler Electricity Supply 230V - 50Hz
Boiler Fuse Rating 2 x External 5A supplies Internal 2AT.4AT (x2)
Power Consumption (boiler only) W 800 800 800 800
Air Inlet O/D m m 110x2 110x2 110x2 110x2
Flue Size dia m m 200 250 250 250
Condensate drain m m 2x21.5 2x21.5 2x21.5 2x21.5
Boiler dry weight (unpacked exc. headers) kg (lb) 336 (740) 396 (874) 430 (948) 466 (1028)
Water Content l (gal) 35 (7.8) 36.8 (8.2) 48.0 (10.6) 54.4 (12.0)
*
*
3
xtra
- Installation & Servicing
GENERAL
xtra
CONTENTS
Boiler Assembly - exploded view. .................................. 11
Boiler Clearances. ............................................................ 9
Boiler Dimensions. ..................................................... 7,8,9
Commissioning and Testing. ......................................... 37
Electrical Connections. .................................................. 18
Electrical Supply. .............................................................. 6
Fault Finding. ................................................................... 50
Flue Installation. ................................................................ 5
Gas Safety Regulations .................................................... 4
Gas Supply. ........................................................................ 4
Hydraulic Resistance. ...................................................... 5
Initial Lighting. ................................................................. 37
Installation. ...................................................................... 11
Option Kits. ........................................................................ 4
Performance Data. ........................................................... 2
Servicing. ........................................................................ 38
Short List of Parts. ......................................................... 54
Ventilation. ........................................................................ 9
Water Circulation. ............................................................ 6
Water Connections. ....................................................... 17
Water System Requirements. ....................................... 10
Water Treatment. ............................................................. 6
Wiring Diagrams. ....................................................... 21,22
Natural Gas only
PI No. 0063 BR 3123
Destination Countries: GB, IE
Key to symbols
IE = Ireland, GB = United Kingdom (Countries of destination)
PMS = Maximum operating pressure of water
C53 = A room sealed appliance which is connected
via its separate ducts to two terminals that
may terminate in zones of different pressure.
C63 = A room sealed appliance intended to be
connected to a separately approved and
marketed system for the supply of
combustion air and discharge of combustion
products. The fan is up stream of the
combustion chamber.
B23 = An appliance intended to be connected to a
flue which evacuates the products of
combustion to the outside of the room
containing the boiler. The combustion air is
drawn directly from the room. The fan is up
stream of the combustion chamber.
NOTE TO THE INSTALLER:
LEAVE THESE INSTRUCTIONS ADJACENT TO THE GAS METER.
4
xtra
- Installation & Servicing
GENERAL
INTRODUCTION
The
xtra
boilers are fully automatically controlled, floor
standing, fanned, super efficient condensing appliances.
The imax xtra comprises of 2 modules, Master and Slave.
The comprehensive boiler controls built into the appliance
include:
- 0-10V Boiler control input
- Volt free 'alarm' contacts (lockout)
- Volt free 'boiler run' contacts
- Burner hours run meters
- System temperature indication
The boilers can draw their combustion air from the room or via
ducting from outside.
Through a sophisticated control system combined with premix
burner technology and an aluminium heat exchanger, the boilers
are capable of high operating efficiencies of 93% (gross) and low
emissions.
These boilers are certified to meet the requirements of the EC
Gas Appliance Directive, Boiler Efficiency Directive, EMC and Low
Voltage Directive.
OPTIONAL EXTRA KITS
•Modulating Sequencer
- DHW Sensor
- Room Sensor
•Programmable Room Stat
•Outside Sensor
(only suitable for use in conjunction with Prog. Room Stat)
•Water and Gas Header Pack
•RS Air Duct Connector (F320 and F400 only)
•Horizontal Flue Header *
•Vertical Flue Header *
* A flue header kit (horizontal or vertical) must be fitted to boiler.
SAFETY
Current Gas Safety (Installation and Use) Regulations or rules in
force
The appliance is suitable only for installation in GB and IE and
should be installed in accordance with the rules in force.
In GB, the installation must be carried out by a CORGI Registered
Installer or in IE by a competent person. It must be carried out in
accordance with the relevant requirements of the:
• Gas Safety (Installation and Use) Regulations
• The appropriate Building Regulations either The Building
Regulations, The Building Regulations (Scotland), Building
Regulations (Northern Ireland).
• The Water Fittings Regulations or Water byelaws in Scotland.
• The Current I.E.E. Wiring Regulations.
Where no specific instructions are given, reference should be
made to the relevant British Standard Code of Practice.
In IE, the installation must be carried out by a Competent Person
and installed in accordance with the current Building Regulations
and reference should be made to the current ETCI rules for
electrical installation.
The boilers have been tested by Gastec and conform to EN483
and EN677 for use with Natural Gas.
Detailed recommendations are contained in the following
Standards and Codes of Practice:
BS. 5854 Flue and flue Structures in Buildings.
BS. 6644 Installation of gas fired hot water boilers of rated
inputs between 70kW and 1.8MW (net) (2nd and
3rd family gases).
BS. 6880 Low temperature hot water heating systems of
output greater than 45kW.
Part 1 Fundamental and design considerations.
Part 2 Selection of equipment.
Part 3 Installation, commissioning and maintenance.
IGE/UP/1 Soundness testing and purging of industrial and
commercial gas installations.
IGE/UP/2 Gas installation pipework, boosters and
compressors on industrial and commercial
premises.
IGE/UP/10 Installation of gas appliances in industrial and
commercial premises.
SAFE HANDLING OF SUBSTANCES
No asbestos, mercury or CFCs are included in any part of the
boiler or its manufacture.
FOUNDATION / LOCATION OF BOILER
The boiler must stand on a floor which must be flat, level and of a
suitable load bearing capacity to support the weight of the boiler
(when filled with water) and any ancillary equipment.
Ideally the boiler should be placed on a plinth exceeding the plan
area of the boiler by 75mm on each side and at least 100mm high.
The boiler must not be fitted outside.
GAS SUPPLY
The local gas supplier should be consulted, at the installation
planning stage, in order to establish the availability of an adequate
supply of gas. An existing service pipe must NOT be used without
prior consultation with the local gas supplier.
A gas meter can only be connected by the local gas supplier or by a
registered CORGI engineer or in IE by a competent person.
An existing meter should be checked, preferably by the gas
supplier, to ensure that the meter is adequate to deal with the rate
of gas supply required. A minimum working gas pressure of
15mbar MUST be available at the boiler inlet for Natural gas.
Do not use pipes of smaller size than the boiler inlet gas
connection.
The complete installation MUST be tested for gas soundness and
purged in accordance with the appropriate standards.
Gas Boosters
A gas booster is required if the gas pressure available at the boiler
is lower than that required by the boiler manufacturer to attain the
flow rate for maximum burner input rating.
Location of the booster requires careful consideration but should
preferably be closer to the burner rather than the gas meter.
Ventilation should also be considered to ensure ambient
temperature do not exceed designed recommendations. Further
guidance is provided in IGE/UP/2.
5
xtra
- Installation & Servicing
GENERAL
FLUE INSTALLATION
The appropriate Ideal Flue Header Kit (veritcal or horizontal)
must be fitted to these boilers.
IMPORTANT. It is the responsibility of the installer to ensure, in
practice, that products of combustion discharging from the
terminal cannot re-enter the building or any other adjacent
building through ventilators, windows, doors, other sources of
natural air infiltration, or forced ventilation / air conditioning.
If this should occur the appliance MUST be isolated from the
gas supply and labelled as 'unsafe' until corrective action can be
taken.
Terminal Position
Due to the high efficiency of the boilers pluming will occur.
Particular care should be taken in the case of large output boiler
installations, and complying with the requirements of the Clean
Air Act.
The flue must be installed in accordance with the appropriate
Building Regulations and standards listed on page 4 and in
compliance with BS6644. In IE refer to I.S.820:2000.
FLUE SYSTEM DESIGN
Due to the high efficiency of these boilers, the flue gas
temperatures are low and the buoyancy in the stack will be
relatively small. The boiler is supplied with an integral fan which
is fully matched to the boiler in each case to provide correct
combustion air flow and overcome the flue resistance.
The power of this fan is such that there is a large reserve of
pressure available to overcome a significant length of flue
without affecting the combustion performance of the boiler. The
maximum pressure available at the base of the flue to overcome
flue resistance is 145Pa (0.58" w.g.) for F320, F400, F480 and
F560. This includes the resistance of any air ducts used to
connect the air inlet direct to outside air. Care should be taken
with tall flue systems to ensure excess buoyancy is not created.
A negative pressure must not be created at the boiler flue outlet.
See table below for approximate maximum straight flue length.
Boiler F320 F400 F480 F560
Flue Size (mm) Ø200 Ø250 Ø250 Ø250
Approx. max.
Straight Flue 109 235 162 116
Length (m)
If the high level air inlet kit, supplied with this appliance, is to be
utilised, the following table shows the approximate maximum
straight flue lengths and pressures available.
Boiler F320 F400 F480 F560
Flue Size (mm) Ø200 Ø250 Ø250 Ø250
Approx. max.
Straight Flue 57 129 67 40
Length (m)
Flue Pressure (Pa) 76 80 60 50
The addition of elbows and their positions in the flue will have a
significant effect on the maximum allowable flue and air duct
lengths. Consult with your flue supplier for detailed design
work.
IMPORTANT NOTE.
If combustion air is drawn from within the boiler room, ensure
no dust or airborne debris can be ingested into the appliance.
Dusty concrete flooring should be sealed to reduce the
presence of dust. Ideally where possible duct the air supply
into the boiler room from a clean source outside the boiler
room / building.
Material
With no requirement for buoyancy to discharge flue products and
with low flue gas temperatures, single wall flues are suitable for
most installations. Care should still be taken to maintain
compliance with building regulations and relevant standards.
The flue used should be a suitably approved flue for use on a
pressurised condensing flue system. Materials choice includes
plastic, aluminium and 316 grade stainless steel. Unless the
flue is manufactured from aluminium, the condensate from
the flue must be collected and drained before entering the
sump of the boiler (when employing the vertical combined flue
outlet header, a flue condensate drain is provided for this
purpose). Advice regarding the availability of proprietary types of
flue system can be obtained by contacting Ideal Stelrad Group.
All joints or connections in the flue system must be impervious
to condensate leakage. Low points in the flue system should be
drained using pipe of material resistant to condensate
corrosion. All drains in the flue should incorporate a water trap.
Care should also be taken in the selection of flue terminals as
these tend to accentuate the formation of a plume and could
freeze in cold weather conditions.
Care should be taken to ensure the specification of the chimney
is suitable for the application by reference to the manufacturers
literature.
6
xtra
- Installation & Servicing
GENERAL
WATER CIRCULATION SYSTEM
A circulation pump MUST be connected to the boiler, see below.
The boiler must NOT be used for direct hot water supply. The
hot water storage cylinder MUST be of the indirect type.
Single feed, indirect cylinders are not recommended and MUST
NOT be used on sealed systems.
The appliances are NOT suitable for gravity central heating nor
are they suitable for the provision of gravity domestic hot water.
The hot water cylinder and ancillary pipework, not forming part of
the useful heating surface, should be lagged to prevent heat
loss and any possible freezing - particularly where pipes run
through roof spaces and ventilated underfloor spaces.
The boiler must be vented. There must be no low points
between the boiler flow connection and a system vent point,
which should be positioned as close as practically possible to
the boiler flow connection.
Draining taps MUST be located in accessible positions, which
permit the draining of the whole system - including the boiler
and hot water storage vessel. They should be at least 1/2" BSP
nominal size and be in accordance with BS. 2879. Do not use
the boiler drain tap to drain the system as this can induce
sludge into the heat exchanger.
The central heating system should be in accordance with the
relevant standards listed on page 4.
Due to the compact nature of the boiler the heat stored within
the castings at the point of shutdown of the burner must be
dissipated into the water circuit in order to avoid overheating. In
order to allow pump operation after burner shutdown the boiler
control box incorporates a 5 minute pump overrun facility. In
order to make use of this, a pump must be supplied from the
terminals inside the boiler. Note: for pumps requiring greater
than 1.0 amp current, they must be connected via a relay.
When sizing pumps, reference should be made to the Hydraulic
Resistance Table on page 6 which show the boiler resistance
against flow rates, to achieve the required temperature
differential.
Flow rates for common systems using either 11oC or 20oC
temperature differentials are given in the table below.
Water flow rate temp. Water flow rate temp.
difference 11oC (20oF) difference 20oC (36oF)
l/s m3/h l/s m3/h
F320 7.14 25.70 3.93 14.15
F400 9.02 32.47 4.96 17.86
F480 10.83 38.99 5.96 21.46
F560 12.63 45.47 6.95 25.02
Note.
• With the boiler firing at maximum rate, the temperature
differential should not be less than 10oC. Higher flow rates
required for lower temperature differentials could lead to
erosion of the heat exchanger water ways.
• With the boiler firing at minimum rate, the temperature
differential should not be greater than 35oC. Lower flow rates
generating higher temperature differentials will lead to lock
out of the boiler.
• The lower the return temperature to the boiler, the higher the
efficiency. At return temperatures of 55oC and below, the
difference becomes marked because the water in the flue
gases starts to condense, releasing its latent heat.
In installations where all radiators have been provided with
thermostatic radiator valves, it is essential that water circulation
through the boiler is guaranteed. A mixing header will perform
this task. Alternatively this can be best achieved by means of a
differential pressure valve, which is installed in a bypass
between the flow and return pipes. The bypass should be fitted
at least 6m from the boiler, and should be capable of allowing a
minimum flow rate to achieve a temperature differential of no
greater than 35oC at minimum rate.
WATER TREATMENT
These boilers incorporate an ALUMINIUM heat exchanger.
IMPORTANT. The application of any other treatment to this
product may render the guarantee of Ideal Stelrad Group
INVALID.
Ideal Stelrad Group recommend Water Treatment in
accordance with Guidance Notes on Water Treatment in Central
Heating Systems.
Ideal Stelrad Group recommend the use of Fernox Copal or
MB1 or GE Betz Sentinel X100 inhibitors and associated water
treatment products, which must be used in accordance with the
manufacturers' instructions.
For further information contact:
Fernox Manufacturing Co. Ltd., Cookson Electronics,
Forsyth Road, Sheerwater, Woking, Surrey, GU21 5RZ
Tel: +44 (0) 1799 521133 or
Sentinel Performance Solutions.,
The Heath Business & Technical Park, Runcorn, Cheshire, WA7 4QX
Tel: 0800 389 4670. www.sentinel-solutions.net
1. It is most important that the correct concentration of the water
treatment products is maintained in accordance with the
manufacturers' instructions.
2. If the boiler is installed in an existing system any unsuitable
additives MUST be removed by thorough cleansing.
3. In hard water areas, treatment to prevent limescale may be
necessary - however the use of artificially softened water is
NOT permitted.
4. Under no circumstances should the boiler be fired before
the system has been thoroughly flushed.
ELECTRICAL SUPPLY
WARNING. This appliance must be earthed.
Wiring external to the appliance MUST be in accordance with the
current I.E.E. (BS7671) Wiring Regulations and any local
regulations which apply. For Ireland reference should be made
to the current ETCI rules for electrical installations.
The point of connection to the mains should be readily
accessible and adjacent to the boiler.
CONDENSATE DRAIN
Condensate drains are provided on the boiler. These drains
must be connected to a drainage point on site. All pipework and
fittings in the condensate drainage system MUST be made of
plastic - no other materials may be used.
IMPORTANT. Any external runs must be insulated to avoid
freezing in cold weather causing blocking.
Boiler Pressure Drop Pressure Drop
(mbar) @ 20oC (mbar) @ 11oC
F320 90 297
F400 95 314
F480 100 330
F560 105 347
HYDRAULIC RESISTANCE
7
xtra
- Installation & Servicing
GENERAL
1
BOILER DIMENSIONS AND CONNECTIONS - HORIZONTAL FLUE CONNECTION KIT
FITTED
All dimensions shown in mm
im9615
Boiler Size
SIDE VIEW FRONT VIEW
PLAN VIEW
REAR VIEW
G (Flow & Return)
17 (Condensate Drain)
110
91 (Gas)
113 (Air Inlet)
Flow
Connections
R2"
Return Connection R2"
Gas R1"
Air Inlet Ducts O110
Slave Module
High Level Air Inlet Kit (If Fitted)
Master Module
8
xtra
- Installation & Servicing
GENERAL
1
CONT'D...BOILER DIMENSIONS AND CONNECTIONS - VERTICAL FLUE CONNECTION
KIT FITTED
All dimensions shown in mm
110
High Level Air Inlet Kit (If Fitted)
Boiler Size
REAR VIEW
Return Connection R2" Air Inlet Ducts O110
Slave Module
Condensate
Drain
Master Module
SIDE VIEW FRONT VIEW
PLAN VIEW
im9616
9
xtra
- Installation & Servicing
GENERAL
2
BOILER DIMENSIONS AND CONNECTIONS
(Optional water and gas header kit and rs air duct connector (F320 & F400 only) fitted)
Note. F320 Model shown
4
VENTILATION
The ventilation requirements of these boilers are dependant
on the type of flue system used, and their heat input. All vents
must be permanent with no means of closing, and positioned
to avoid accidental obstructions by blocking or flooding.
Detail reference should be made to BS. 6644 for inputs
between 70kW and 1.8MW (net). In IE refer to the current
edition of I.S.820. The following notes are for general
guidance only:
Dust contamination in the combustion air may cause blockage
of the burner slots. Unless the boiler room provides a dust
free environment then direct connection of the air intake via
ducting to clean outside air should be used.
IMPORTANT NOTE.
If combustion air is drawn from within the boiler room,
ensure no dust or airborne debris can be ingested into the
appliance. Dusty concrete flooring should be sealed to
reduce the presence of dust.
The temperature within a boiler room shall not exceed 25oC
within 100 mm of the floor, 32oC at mid height and 40oC within
100 mm of the ceiling.
Open Flued Installations
If ventilation is to be provided by means of permanent high and
low vents communicating direct with outside air, then reference
can be made to the sizes below. For other ventilation options
refer to BS. 6644. In IE refer to the current edition of I.S.820.
Required area (cm2) per kW of total rated input (net)
Boiler Room Enclosure
Low level (inlet) 4 10
High level (outlet) 2 5
Note: Where a boiler installation is to operate in summer
months (e.g. DHW) additional ventilation requirements are
stated, if operating for more than 50% of time (refer to BS6644).
Room Sealed Installations
A minimum of 2cm2free area per kW of net heat input at both
high and low level is required for boiler rooms. For enclosures
refer to BS6644.
3
BOILER CLEARANCES
The minimum dimensions as indicated must be respected to
ensure good access around the boiler.
Recommended minimum clearances are as follows.
Rear: 1000mm or adequate space from the rear of the jacket
to make the flue connections and access to the flue sample
point, drain connection, flue and any safety or control devices.
All dimensions shown in mm
SIDE VIEW
im9159
REAR VIEW
Flow
connection
Return
connection
Left Side: 450mm
Right Side: 450mm
Front: 600mm; except, access doors may be closer, but
not less than 200mm and 600mm must still be available
for service across the width of the boiler.
Top: 500mm.
10
xtra
- Installation & Servicing
GENERAL
Rated output Minimum bore Nominal Size (DN)
kW m m in
301 to 600 50 2
'Steel pipe sizes complying with medium or heavy quality or BS 1387.
Detail reference should be made to the appropriate standards listed on
page 4.
The information and guidance given below is not intended to override any
requirements of the above publications or the requirements of the local
authority, gas or water undertakings.
The vertical distance between the pump and feed/expansion cistern MUST
comply with the pump manufacturer's minimum requirements, to avoid
cavitation. Should these conditions not apply either lower the pump
position or raise the cistern above the minimum requirement specified by
Ideal Stelrad Group. The isolation valves should be fitted as close to the
pump as possible.
The information provided is based on the following assumptions:
1. An independent open vent/safety pipe connection is made immediately
after the system flow pipe connection.
2. An independent cold feed/expansion pipe connection is made
immediately after the open vent/safety pipe connection.
3. The maximum flow rate through the boiler is based on a temperature
difference of 11oC at full boiler output.
4. The boiler is at the highest point of circulation in the system. Systems
designed to rise above the boiler flow tappings will automatically
require a minimum static head higher than that shown.
5. The position of the open vent/safety pipe above the expansion cistern
water level is given as a guide only. The final position will depend upon
the particular characteristics of the system. Pumping over of water into
the expansion cistern must be avoided.
6. Both open vent/safety pipe and cold feed/expansion pipes must be of
adequate diameter to suit the output of the boiler. Refer to Tables
below and BS 6644:2005.
5
OPEN VENTED SYSTEM REQUIREMENTS
Note.
• With a cold feed head of <8m, the pump
must be fitted on the return to the boiler.
• This diagram does not show safety valves,
water flow switches, etc. necessary for the
safe operation of the system.
6
SEALED SYSTEM REQUIREMENTS
Open Vent Pipe Sizes
Rated output Minimum bore Nominal Size (DN)
kW m m in
301 to 600 38 1 1/2
'Steel pipe sizes complying with medium or heavy quality or BS 1387.
Cold Feed Pipe Sizes
Note. Refer to Frame 29 for typical system arrangements.
Feed/expansion
cistern
Open vent
safety pipe
3 m
minimum
see notes
System
flow
Shunt Pump
(if required)
Inverted
cold feed
entry
Cold
Feed
Water
level
(cold)
Open vent
System
return
im8250
Connections
to boiler
Working pressure 6 bar maximum.
Particular reference should be made to BS. 6644 and
Guidance note PM5 "Automatically controlled steam and hot
water boilers" published by the Health and Safety Executive.
The information and guidance given below is not intended to
override any requirements of either of the above publications or
the requirements of the local authority, gas or water
undertakings.
In general commercial closed pressurised systems are
provided with either manual or automatic water make up.
In both instances it will be necessary to fit automatic controls
intended to protect the boiler, circulating system and ancillary
equipment by shutting down the boiler plant if a potentially
hazardous situation should arise.
Examples of such situations are low water level and operating
pressure or excessive pressure within the system. Depending
on circumstances, controls will need to be either manual or
automatic reset. In the event of a shutdown both visual and
audible alarms may be necessary.
Expansion vessels used must comply with BS. 4814 and must
be sized on the basis of the total system volume and initial
charge pressure.
Initial minimum charge pressure should not be less than 0.5
bar (7.2psi) and must take account of the static head and
specification of the pressurising equipment. The maximum
water temperatures permissible at the point of minimum
pressure in the system are specified in Guidance Note PM5.
When make up water is not provided automatically it will be
necessary to fit controls which shut down the plant in the event
of the maximum system pressure approaching to within
0.35bar (5psi) of the safety valve setting.
Other British Standards applicable to commercial sealed
systems are:
BS. 6880: Part 2
BS. 1212
BS. 6281: Part 1
BS. 6282: Part 1
BS. 6283: Part 4