LifeSafety Power F8 User manual

LifeSafety Power, Inc. | PH 888.577.2898 | TechSupport@LifeSafetyPower.com
P03-019 Rev A01
F8 / F8P Installation Manual

F8 / F8P Installation Manual
2 3
Connecting the Power Distribution Module
hRemove all AC and battery power from the FPO system before adding or replacing an F8 module.
FLEXIOFLEXIO FLEXIOFLEXIO
FlexIO continues to other accessories
FlexIO in from System
OUT1 OUT2 OUT3 OUT4 OUT5 OUT6 OUT7 OUT8
F8/F8P
B1
B2
B1
B2
BR
BR
Main DC voltage continues to
other accessories
Second DC Source continues to
other accessories
BR continues to other accessories
DC OUT terminals to devices to be powered
BR in from System
Input from Main
DC voltage source
Input from Second
DC source (optional)
Required Connections
Optional Connections
Each of the B1, B2, BR, and FlexIO busses has two connectors.
These connectors may be used interchangeably.
For example: FlexIO from the power supply may be connected
to either of the F8's FlexIO connectors, the Main DC voltage
source may connect to either B1 terminal, etc.
Description
The F8 FAI controlled distribution accessory provides eight
zones of fused or PTC-protected power distribution with FAI
control. The F8 accepts one or two DC power inputs, either
of which are available on any output zone. Each output is
also selectable for continuous output, enable on FAI, or dis-
able on FAI. The suffix "P" added to the model number de-
notes Class 2 Power limited outputs.
Specifications
Input (per Buss) Voltage 12 or 24VDC nominal +/- 15%
Current 20A maximum
Standby Current 75mA maximum
Output (per Zone) Voltage Same as input
Current (F8) 3A
Current (F8P) 2.5A (Class 2 Power Ltd)
INote that the total current draw from any
buss must not exceed the capability of the
power supply powering that buss.
Fuse (F8) 3A ATM automotive style
Size F8/F8P 4.00" x 2.50" x 1.25"
(102mm x 64mm x 32 mm)
Weight F8/F8P 0.20lb (0.09kg)
Regulatory Information
The equipment discussed within this manual has been tested
to the following standards:
• UL294, UL603, UL1076
• ULC S318, ULC S319
Mounting the F8 Power Distribution Module
Mounting of the board to an enclosure is via the four
snap-in standoffs supplied.
1. Locate the appropriate
mounting holes in the
enclosure and snap
the standoffs into the
holes.
2. Align the board mount-
ing holes with the
standoffs (be sure the PC board is properly oriented)
and snap the board onto the standoffs.
I
For UL Compliance Any locking device shall be configured for
fail-safe operation upon occurrence of an alarm

F8 / F8P Installation Manual
2 3
Accessory Overview
B1
B2
B1
B2
BR
JP2 JP3 JP4 JP5 JP6 JP7 JP8
+ –
OUT1
+ –
OUT2
+ –
OUT3
+ –
OUT4
+ –
OUT5
+ –
OUT6
+ –
OUT7
+ –
OUT8
1
6
1
6
1
6
1
6
1
6
1
6
1
6
1
6
FLEXIOFLEXIOFLEXIOFLEXIO
F1 F2 F3 F4 F1 F2 F3 F4
B2
B1
JP1
FAI
1
FlexIO Connectors
These connectors pass the FAI and Fault signals to and
from the F8 board and pass the FlexIO buss on to other
accessory boards in the system.
2
B1 Connectors (J1 & J4)
These fastons are for connection to the B1 voltage buss in
the system.
The voltage on the B1 buss comes from the DC1 faston
of an FPO power supply. This voltage will be directed to
any outputs whose Output Selection Jumper is set in
one of the B1 positions.
3
B2 Connectors (J3 & J5)
These fastons are for connection to the B2 voltage buss
in the system.
The voltage on the B2 buss comes from the DC1 faston
of an FPO power supply or the DC OUT faston of a B100
secondary power supply in a dual voltage system. This
voltage will be directed to any outputs whose Output
Selection Jumper is set in one of the B2 positions. If
the F8 is being used in a single voltage system, these
fastons can be left unused.
4
Output Selection Jumpers (JP1 – JP8)
These jumpers select which voltage buss input is selected
for the output and the FAI operation for the zone. Jumper
numbers correspond with the zone number (e.g. JP1 is the
jumper for OUT1). Possible settings are as follows:
• Pos. 1 (Top) Constant output of B1 voltage
• Pos. 2 B1 voltage Enables on FAI
• Pos. 3 B1 voltage Disables on FAI
• Pos. 4 Constant output of B2 voltage
• Pos. 5 B2 voltage Enables on FAI
• Pos. 6 (Bot.) B2 voltage Disables on FAI
• Removed Disable Output
5
B2 LED (D4) – Green
This LED indicates the availability of voltage on the B2 Buss.
When voltage is available on the buss, the LED is lit. Note: This
LED will not light in a single voltage system - this is normal.
6
B1 LED (D3) – Green
This LED indicates the availability of voltage on the B1
Buss. When voltage is available on the buss, the LED is lit.
7
BR Connectors (J3 & J6)
The DC Common buss in the system. All boards in the
system must have their BR fastons wired together for
proper operation (except for between the DC and AC
sections of an FPX hybrid system).
8
Zone Outputs (Out1 – Out8)
These are the zone output terminal strips. These ter-
minal strips are removable and accept wire sizes from
AWG14 – AWG22. The terminals are labeled on the PC
board underneath the terminal strip.
ICAUTION When powering magnetic loads such as
maglocks, door strikes, solenoids, etc, each of these
loads must have a reverse protection diode either built-in
or external to the device.
9
FAI LED (D11) – Red
This LED indicates the receipt of an FAI input signal
from the FPO power supply. When FAI is active, the LED
is lit.
bk
Output Fuses (F1 – F8) – Optional
When using the fused version of the F8, these are the fuses
for each zone output. Fuse numbers correspond with the
zone number (e.g. F1 is the fuse for OUT1). When using
the PTC version of the F8, the fuse will be replaced with a
soldered-in PTC.

F8 / F8P Installation Manual
4 5
Single Voltage with Eight Zones of FAI Controllable Distribution
In this application, each Zone Output of the F8 may be set for 24V Continuous Output, 24V Enable on FAI, or 24V Disable
on FAI. Since this is a single voltage system, only jumper Positions 1-3 are valid. FAI Control on the F8 is achieved by
opening the NC Contact on the FPO's FAI Input.
Dual Voltage using Two FPO's with Eight Zones of FAI Controllable Distribution
In this application, each Zone Output of the F8 may be set for 12V or 24V with a Continuous Output, Enable on FAI, or
Disable on FAI. FAI Control on the F8 is achieved by opening the NC Contact on the FPO's FAI Input.
DC1DC1
DC2DC2
BRBR
FPO switch set for 24V
FPO
FPO
FlexIO connectionFlexIO connection
24V Out
FlexIOFlexIO
FlexIOFlexIOB1
B2
F8
Each Zone Output may be set for
Continuous or FAI Operation
BR
B1
B2
BR
FAI INPUTFAI INPUT
LLLLV–V– I–I– I+I+ V+V+
NC
Contact
DC1DC1
DC2DC2
BRBR
FPO switch set for 24V
FPO
FPO
FlexIO connectionFlexIO connection
FlexIO connectionFlexIO connection
24V Out
FlexIOFlexIO
FlexIOFlexIO
B1
B2
F8
Each Zone Output may be set for 12 or 24V
Continuous or FAI Operation
BR
B1
B2
BR
FAI INPUTFAI INPUT
LLLLV–V– I–I– I+I+ V+V+
NC
Contact
DC1DC1
DC2DC2
BRBR
FPO switch set for 12V
FPO
FPO
12V Out
FlexIOFlexIO

F8 / F8P Installation Manual
4 5
Dual Voltage using B100 with Eight Zones of FAI Controllable Distribution
In this application, each Zone Output of the F8 may be set for 12V or 24V with a Continuous Output, Enable on FAI, or
Disable on FAI. FAI Control on the F8 is achieved by opening the NC Contact on the FPO's FAI Input.
– OUT +
DC IN
BR BR
DC OUT
DC IN
DC OUT
B100
Each Zone Output may be set for 12 or 24V
Continuous or FAI Operation
B1
B2
BR
B1
B2
BR
F8
12V OUT
B100 - 12V
DC1DC1
DC2DC2
BRBR
FPO switch set for 24V
FPO
FPO
FlexIOFlexIO
FlexIO connectionFlexIO connection
FlexIO connectionFlexIO connection
FlexIOFlexIO
24V Out
FlexIOFlexIO FAI INPUTFAI INPUT
LLLLV–V– I–I– I+I+ V+V+
NC
Contact

F8 / F8P Installation Manual
6 PB
Section
FlexPower System Replacement Parts
Board Kits Order # Description
FPO250 A01-007 FPO250 replacement board
FPO150 A01-005 FPO150 replacement board
FPO75 A01-003 FPO75 replacement board
B100 A03-009 DC-DC Converter (12VDC or adjustable 5 to 18VDC) replacement board
D8 A02-001 Simple distribution replacement board
D8P A02-002 Simple distribution (Class 2) replacement board
F8 A02-003 FAI controlled distribution replacement board
F8P A02-004 FAI controlled distribution (Class 2) replacement board
C4 A02-005 Four zone power control replacement board
C4P A02-006 Four zone power control (Class 2) replacement board
C8 A02-007 Eight zone power control replacement board
C8P A02-008 Eight zone power control (Class 2) replacement board
M8 A02-011 Eight zone managed power control replacement board
M8P A02-012 Eight zone managed power control (Class 2) replacement board
N24 A04-001 Two Input, 4 Output NAC Expander accessory replacement board
NL2 A11-007 Two Port NetLink network communication board (used in FPO systems)
NL4 A11-004 Four Port NetLink network communication board (used in FPO systems)
NLR A11-002 NetLink network communication kit / remote reset (used in FPA systems)
NS2 A11-003 Reset module board for use with NL2
RB2 A25-001 2A Relay, 12VDC or 24VDC input range, DP/DT
RB5 A25-002 5A Relay, 12VDC or 24VDC input range, DP/DT
RB8 A25-003 8A Relay, 12VDC or 24VDC input range, DP/DT
Hardware Order # Description
DL1 A05-001 DataLink USB cable
BDM A05-006 Battery Disconnect Module cable
AC Cable A05-005 AC Input Cable for FPO Power Supply
Battery Cable A05-002 Battery Harness – 24"
Module Cable - 12" A05-003 Accessory board cable set – 12"
Module Cable - 18" A05-004 Accessory board cable set – 18"
Fuse - 3A A05-201 ATM-3A Fuse – Bag of 25
Fuse - 5A A05-202 ATM-5A Fuse – Bag of 25
Fuse - 7.5A A05-203 ATM-7.5A Fuse – Bag of 25
Fuse - 10A A05-204 ATM-10A Fuse – Bag of 25
Fuse - 15A A05-205 ATM-15A Fuse – Bag of 25
Fuse - 30A A05-206 ATM-30A Fuse – Bag of 25
Standoffs A05-301 Nylon Standoffs – Bag of 25
Camlock Set A05-302 Key and Lock fits LSP "E" enclosure
P03-019 Rev A01 10/16
Important: All information, including illustrations, is believed to be reliable. Users, however, should independently
evaluate the suitability of each product for their particular application. LifeSafety Power makes no warranties as to the
accuracy or completeness of the information, and disclaims any liability regarding its use. LifeSafety Power’s only ob-
ligations are those in the LifeSafety Power Standard Terms and Conditions of Sale for this product, and in no case will
LifeSafety Power or its distributors be liable for any incidental, indirect, or consequential damages arising from the
sale, resale, use, or misuse of the product. Specifications are subject to change without notice. In addition, LifeSafety
Power reserves the right to make changes—without notification to Buyer—to processing or materials that do not affect
compliance with any applicable specification.
LifeSafety Power, FlexPower, NetLink, GreenSmart, FlexConnect, PowerCom, Reliability+, SureCharge, TruWatt, and VSelect are
trademarks or registered trademarks of LifeSafety Power Inc. or its affiliates.
© 2016 LifeSafety Power, Inc.All rights reserved
LifeSafety Power Inc.
304 Terrace Drive
Mundelein, IL 60060 USA
www.lifesafetypower.com
Tel (888) 577-2898
info@lifesafetypower.com
This manual suits for next models
1
Table of contents
Other LifeSafety Power Power Distribution Unit manuals