WISE CONTROL
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 1/10
ITEM : Sight Glass & Flow Indicator
19F, 181, Gasan digital 1-ro, Geumcheon-gu, Seoul, Republic of Korea
Tel : +82-2-300-2300 ; Fax : +82-2-300-2301
WISE CONTROL
1. INTRODUCTION FOR USAGE OF FLOWMETER
1) GENERAL
2) INSTALLATION
2. SIGHT GLASS AND FLOW INDICATOR
1) GENERAL
2) STANDARD FEATURE
3) CHARACTERISTICS
4) INSTALLATION AND MAINTENANCE
5) TROUBLESHOOTING
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 2/10
CONTENTS
WISE CONTROL
1. General
and it is called "Flowmeter Diagram"
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 3/10
INSTRUCTION FOR USAGE OF FLOWMETER
For the correct usage of the Flowmeter, Installation, Maintenance, Repair and Inspection
shall be done at the site. No matter how excellent in the design and best parts applied
in the Flowmeter, not only the flowmeter is bad in its performance but also the whole
system is low in the creditability and safety without good consideration on the Process,
and well organized work control and maintenance plan.
Hence, due to the Carelessness in installation and maintenance of the Flowmeter in the
Process can cause the bad performance or malfunction of the whole system, the correct
installation and proper maintenance program shall be set up as a part of the Process
and executed by the plan.
2. Installation
(1) Flometer Diagram
It is designed the basic piping diagram to maximize the performance of the flowmeter,
As shown on Fig.1-1, each entity has own role and is required for the accurate
measurement of the flow rate. But, the actual "Flowmeter Diagram"can be differed by
the principle of the applied flowmeter and the fluid flow to be measured, then please
refer this manual carefully to make the proper diagram. Also simple explanations for
each entity are added.
WISE CONTROL
①AMBIENT TEMPERATURE
⑥Avoid in the piping occurred the cavitation effect.
⑦Must keep the required straight line length by the type of the flowmeter.
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 4/10
(2) Installation Condition
For the accurate and consistent measurement, it is recommended to install the
flowmeter with cautions as the below.
▷Install the Flowmeter at the place where the temperature keep in constant or
change in small.
▷The allowable temperature in the installed place shall be complied to the
Specification of the Flowmeter.
②ATMOSPHERE
▷Avoid the place existing the corrosive gas.
▷Don't let the water flow into the conduit or stay in.
③Install at the place without or minimized the shock and vibration.
④Keep enough space for the maintenance and repair.
⑤Avoid the place existing Electromagnetic Interference.
WISE CONTROL
turbulence and axial flow.
It will be explained in detail at the provisions for the principle of the flowmeter,
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 5/10
to the installation.
of the problem, the investigation of the cause, resolutions and prevention in future.
of the malfunction and defect, which is being kept in record, and Occasional
Check-out of the cleanness and tightness. Post Program is designed for the reactive
of the flowmeter after the malfunction occurred and is included in the understands
(3) Installation
It shall be installed by the instruction specified and flushed the flowmeter prior
to the installation.
①Confirm the flow direction with the indication on the flowmeter.
②Use the correct size of the tightening bolts with the Pipe.
③Install the seal such as gasket to prevent from leaking.
④Tighten the bolts with the constant force and the diagonal directional sequence.
⑤Follow the specified earthing method in electrical works.
(refer to the attached wiring diagram)
(4) Maintence and Check
Generally the maintenance program can be classified by two types; Precautionary
program and Post program.
In Precautionary program, it is included in the Internal Check List for the precaution
maintenance and checking method for each type of the flowmeter.
①Seperator
This is the device to reduce the error on reading due to the air or steam
included in the fluid flow. It shall be applied in the system using the mass flowmeter.
②Strainer (Filter)
This is the device to prevent the damage by collecting the dust, chips, sand or
other foreign substances in the fluid flow.
③Flow Conditioner
The is the device installed at the upstream of the flowmeter in order to minimize
the effects on the flowmeter characteristics by removing or reducing the vortex,
WISE CONTROL
of the flowmeter for the accuracy of the measurement. This part is required to
make the flow stable, and a priority factor to be considered in the design of the
piping line.
It is recommended to design the Piping Line that the maintenance, repair, inspect
If the flow control V/V was placed in upstream of the flowmeter, it could be
interfered to the flow and the correct measurement could not expected. Hence, it
enough distance from the flowmeter to prevent from effecting on the flow, if
installed in upstream.
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 6/10
and calibration of the flowmeter can be done without stopping of the PROCESS.
is recommended to install the flow control V/V in downstream, or keep the
④Straight Piping Line
It is the straight part of the piping line between the upstream and downstream
⑤By-Pass Line
⑥Flow Control Valve
WISE CONTROL
1. General
The flow rate can be obtained by measuring the Pressure difference of the flow through
the FLAPPER & Spring tension Interrelation and flow measurement.
This type of Flowmeter has some advantages such as simple structure, easy to handle
and wide application from small to large flow.
2. Standard Feature
(1) DIAMETER : 1" - 20"
(2) TEST PRESSURE : 10Kgf/㎤G(Max),Option (20kgf/㎠2)
(3) MAX. OPERATING TEMP : 120℃
(4) ACCURACY : F․S ±5%
3. Characteristics
(1) Simple and clear reading the instant flow in piping.
(2) Simple structure and easy installation.
(3) Compact size and available for the large flow measurement.
4. Installation and Maintence
(1) Install the Flowmeter in matching the Measuring Part with the direction of flow.
(2) Clean up the GLASS Inside periodically (including Strainer)
(3) Connect the Measuring Part in Straight Piping Line
( IN Let = 3D ~ 20D Length, OUT Let = 3D ~ 5D Length)
(4) For the repair or cleaning of the Indicator, add the BY Pass function.
INSTALLATION & OPERATION
MANUAL
SIGHT GLASS AND FLOW INDICATOR (F850)
DOC.NO. : C-QIM-2731-F14
PAGE : 7/10
WISE CONTROL
5. Troubleshooting
※Prior to install the Flowmeter, Flushing the Piping Line shall be done.
The Strainer is recommended to install in the front of Flowmeter.
Q. Incorrect Buoyant of Rota in Gauge.
A1. Check the Flow first.
A2. In measuring the gas, check the operating pressure with the Flowmeter
Operating Pressure.
< Flowmeter Operating Pressure is called the pressure on the of the Flowmeter>
A3. Check the clogging inside of Body & Indicator to cause the Pressure Loss.
A4. Dismount the Strainer and Clean.
A5. Check the Limit Stopper of Flow.
(Open the Upper CAP, and check the clogging of hole on the Upper Limit Stopper
in Glass.)
Q. Leak between the glass and Connection to BODY.
A1. Check the omission of the seal (packing) between the Indicator and Connection.
A2. Tighten down the Indicator tight bolts
Q. Impossible to read the Flow rate
A1. Open the Upper cover and disassemble the GLASS.
Clean the inside of GLASS with soft cloths or brush.
Q. Leak in the FLANGE Part
A. Tighten down the connecting bolts.
A. Check the omission of PACKING
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 8/10
WISE CONTROL
1. General
When flow of liquid come by difference pressure from pipe line inside have a flapper on
use measuring flow.
Simple design and treatment use for medium or large flow late.
F851 is application under favor of come by difference pressure from flapper and
spring tension.
2. Standard Feature
(1) DIAMETER : 1/2" - 6"
(2) TEST PRESSURE : 10Kgf/㎤G(Max)
(3) MAX. OPERATING TEMP. : 60℃
(4) ACCURACY : F․S ±5%
3. Characteristics
(1) It's can simplicity read inside of pipeline.
(3) Small size use can measuring large flow rate
(4) Easy for installation
(5) Easy for maintenance.
4. Installation and Maintenance
(1) When installation of flow meter doing in one flow direction.
(flow direction is installation an arrow on the body)
(2) Must be use the straight line for flow meter.
(IN Let = 3D ~ 20D , OUT Let = 3D ~ 5D)
(3) When out of order instrument and cleaning added function of by-pass.
(4) It's installation strainer for dregs and sludge
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 9/10
(2) It's Simple design and convenient to handle .
SIGHT GLASS AND FLOW INDICATOR (F851)
WISE CONTROL
5. Troubleshooting
※Installation before must be cleaning.
It is possible installation strainer.
Q. An incorrect indicating
A1. Check of the regularity flow liquid.
A2. in case of gas check of the working pressure with standard pressure
< working pressure is posterior to installation flow meter >
A3. check dregs and sludge of the inside flow meter
A4. cleaning to the strainer
Q. In case of come by connection part leakage
A1. Check of the connection part o-ling.
A2. Instrument part BOLT (M6*25 hexagon BOLT)screw up
Q . When illegible flow rate
A1. Instrument part separate from body.
Soft cloth and brush use wiping inside body
Be careful lost o-ling and prat of item
Assemble in reverse order
A. Strong screw up companion bolt
A. Check of the packing or gasket
INSTALLATION & OPERATION
MANUAL
DOC.NO. : C-QIM-2731-F14
PAGE : 10/10
Q. In case of come by body part leakage

Other Wise Measuring Instrument manuals

Wise P710 User manual

Wise

Wise P710 User manual

Wise P510 Series User manual

Wise

Wise P510 Series User manual

Wise P810 User manual

Wise

Wise P810 User manual

Wise P660 Series User manual

Wise

Wise P660 Series User manual

Wise SMT3000 User manual

Wise

Wise SMT3000 User manual

Wise T500 Series User manual

Wise

Wise T500 Series User manual

Wise P257 User manual

Wise

Wise P257 User manual

Wise P620 Series User manual

Wise

Wise P620 Series User manual

Wise T110 User manual

Wise

Wise T110 User manual

Wise P751 User manual

Wise

Wise P751 User manual

Wise P670 User manual

Wise

Wise P670 User manual

Wise GM-1000 User manual

Wise

Wise GM-1000 User manual

Wise F510 User manual

Wise

Wise F510 User manual

Popular Measuring Instrument manuals by other brands

wtw TetraCon 700-...Ex Series operating manual

wtw

wtw TetraCon 700-...Ex Series operating manual

Fortis 4063726007728 manual

Fortis

Fortis 4063726007728 manual

Oceanic Systems 5700 user manual

Oceanic Systems

Oceanic Systems 5700 user manual

Inficon HAPSITE ER operating manual

Inficon

Inficon HAPSITE ER operating manual

MRC DBD-001N Operation manual

MRC

MRC DBD-001N Operation manual

TCTEC Mini Touchscreen Voice Recorder user manual

TCTEC

TCTEC Mini Touchscreen Voice Recorder user manual

AccuEnergy EV300 Series user manual

AccuEnergy

AccuEnergy EV300 Series user manual

Michell Instruments ES70 user manual

Michell Instruments

Michell Instruments ES70 user manual

SenTech iSOBER 30 user manual

SenTech

SenTech iSOBER 30 user manual

Blue-White industries F-2000 instruction manual

Blue-White industries

Blue-White industries F-2000 instruction manual

Bosch GAM 270 MFL Operating/safety instructions

Bosch

Bosch GAM 270 MFL Operating/safety instructions

Autonics MP5S Series instruction manual

Autonics

Autonics MP5S Series instruction manual

Chauvin Arnoux CA 1730 user manual

Chauvin Arnoux

Chauvin Arnoux CA 1730 user manual

Bender RCMA426H manual

Bender

Bender RCMA426H manual

Mitutoyo LGF-110ZL-B quick start guide

Mitutoyo

Mitutoyo LGF-110ZL-B quick start guide

triOS OSCAR G2 manual

triOS

triOS OSCAR G2 manual

VTI Instruments EMX-4250 user manual

VTI Instruments

VTI Instruments EMX-4250 user manual

Hesai PandarXT-16 user manual

Hesai

Hesai PandarXT-16 user manual

manuals.online logo
manuals.online logoBrands
  • About & Mission
  • Contact us
  • Privacy Policy
  • Terms and Conditions

Copyright 2025 Manuals.Online. All Rights Reserved.