Fire Alarm Systems | F220 Photoelectric Smoke Detectors
F220 Photoelectric Smoke Detectors
www.boschsecurity.com
uTwo-wire or four-wire bases
u30 ft (9 m) maximum spacing between detectors
uOptional CO-sensor, heat-sensor enhanced
detection chamber
uClean chamber without removal or disassembly
uCleanMe signaling capability
The F220 Photoelectric Smoke Detectors are UL
Listed, open-area photoelectric smoke detectors. Use
them with commercial fire protective signaling
systems and household fire warning systems (see
NFPA 72, the National Fire Alarm Code). These smoke
detectors scatter light using a pulsed infrared source
operating with a gated, high-speed, photodiode
infrared sensor. The symmetry of the optical chamber
allows 360° uniform smoke entry, but minimizes
external light entry. The detectors use low current
electronic circuitry, so they can connect to 12 VDC
nominal or 24 VDC nominal power source circuits.
Functions
Compatible Bases
Configure the detectors into two-wire or four-wire
versions by selecting the appropriate mounting base.
These detectors are compatible with any of the
F220‑B6 bases:
•F220-B6 12/24 VDC Two‑wire Mounting Base
• F220-B6R Standard 12/24 VDC Four‑wire Mounting
Base
• F220-B6RS 24 VDC Four‑wire Mounting Base with
Sounder
• F220-B6C 12/24 VDC Four‑wire Mounting Base with
Auxiliary Relay
• F220-B6E 12/24 VDC Four‑wire Power Supervision
Mounting Base
•F220-B6PM 24 VDC Four‑wire Addressable Master
Base
• F220-B6PS 12/24 VDC Four‑wire Addressable Base
Monitoring the Detection Chamber
These detectors have several features that work
together to maximize the performance of the optical
chamber:
•Compensation: The detector monitors the chamber
for the effects of dust build-up within the chamber
and automatically compensates for these effects. If
the chamber becomes contaminated beyond its
ability to compensate, the green LED flashes every
4 sec to indicate trouble.
•Chamber Check Self-diagnostics: The detector
automatically indicates visually if the calibration is out
of the factory-listed range. This meets NFPA
guidelines for sensitivity testing, because you can
visually inspect the detector and check the flash rate
of the LED. If the calibration is out of range, the green
LED on the detector flashes once every 4 sec. This
indicates that the detector must be cleaned following
the instructions provided with the detector.
•CleanMe Mode: Indicates if the calibration is out of
the factory-listed range by sending a trouble signal to
the CleanMe-compatible control panel, if so
programmed.
•Chambermaid: The detector has a unique cleaning
mechanism. Use the valve on the back of the detector
to insert the nozzle of a can of clean, dry compressed
air. Clean the chamber with a short (1 to 2 sec) blast
of air.
Heat and Carbon Monoxide Enhancements
The detectors are available with an optional fixed-
temperature heat sensor, a carbon monoxide (CO)
sensor, or a combination of heat and CO sensors.
These optional sensors enhance the operation of the
smoke detector by reducing false alarms.
•Carbon Monoxide: Without the presence of CO, a
normal byproduct of combustion, the detection
chamber is half as sensitive to smoke as a standard
commercial photoelectric smoke chamber. This
reduces false alarms. When the sensor detects CO,
the detection chamber's sensitivity to smoke
increases so it equals or exceeds that of a standard
commercial photoelectric smoke chamber.
Notice
The F220-PTHC detects carbon monoxide (CO) as
a component of a fire. It is not a CO detector and
cannot activate an alarm in the presence of CO
only.
•Heat: When the heat sensor detects a temperature
rise, the photoelectric chamber becomes more smoke
sensitive. The heat sensor initiates an alarm if the
ambient temperature exceeds +135°F (+57°C).
Dual-color LED
A dual-color LED indicator flashes green every 8 sec
when the detector has power and the smoke sampling
circuitry is working. If CleanMe is enabled, the green
LED double flashes (two flashes a half second apart)
every 8 sec to indicate normal operation. The LED
turns red if an alarm is sent. After the alarm condition
clears, reset the detector by interrupting its power. If
the chamber becomes contaminated beyond its ability
to compensate, the green LED flashes every 4 sec to
indicate trouble.
Test Functions
The F220 Photoelectric Smoke Detectors feature a
unique magnet operation and sensitivity test function.
Test the detector's operation by placing the magnet
next to the detector's LED for three consecutive
flashes. This causes the detector to send an alarm.
Placing a magnet next to the detector's LED for at
least one red flash but less than three flashes activates
the detector's sensitivity mode.
Tamper Detection
When detector heads are correctly installed in any of
the F220-B6 bases, the positive power line provides
tamper detection. The control panel initiates a trouble
signal if a detector is removed from its base. A
mechanical tamper lock comes with each base to
prevent unauthorized head removal.
Certifications and approvals
Region Certification
Europe CE 89/336/EEC, EN50130-4/A Sept 1998,
EN61000-6-3 Oct 2001
USA UL UROX: Smoke-automatic Fire Detectors
(ANSI/UL 268), UROX7: Smoke-auto-
matic Fire Detectors Certified for Cana-
da (CAN/ULC-S529)
FM
CSFM 7272-1615: 0106 [F220-P, F220-PTH]
CSFM 7272-1615:0107 [F220-PTHC]
NYC-
MEA
117-05-E
MSFM 2200 Sep 2008
Hong Kong HKFSD
Installation/configuration notes
Compatible Control Panels
Addressable Systems: compatible with addressable
systems controlled by D9412GV2, D7412GV2,
D9412G, or D7412G Control Panels or the D9124 Fire
Alarm Control Panel when used with the F220-B6PM
or F220-B6PS Addressable Detector Bases.
Two-wire: Bosch Security Systems, Inc. makes no
claim written, oral, or implied that the F220
Photoelectric Smoke Detectors work with any two-
wire control panels except those specified in the
Control Panel Compatibility chart in the Technical
Service Note (P/N: 4998148185).
Four-wire: compatible with all UL Listed four-wire
control panels. Refer to the control panel's installation
instructions for proper end-of-line (EOL) resistor
selection.
Mounting the Bases
Notice
Consult NFPA‑72 for proper detector placement.
Depending on local regulations, the bases can be
surface mounted directly on four-inch square or
octagonal electrical boxes and single-gang switch
boxes.
Notice
The volume of any electrical box used should be
large enough to accommodate the number and
size of conductors as specified by the National
Electrical Code or any local authorities having
jurisdiction (AHJ).
2 | F220 Photoelectric Smoke Detectors
Loop Supervision
Loop supervision requires one D275 or F220-B6E per
loop when using F220‑B6R/B6C bases and is
supervised by the control panel.
Wiring the Bases
Refer to the F220 Series Detectors with
F220‑B6/C/E/R Bases Installation Instructions
(P/N: 4998138694), the F220 Series Detectors with
F220‑B6RS Bases Installation Instructions
(P/N: F01U029847), or the F220-B6PS/M Installation
Instructions (P/N: 4998149982) for detailed wiring
instructions.
Technical specifications
Environmental Considerations
Relative Humidity: 0% to 95% non-condensing;
15% to 95% non-condensing for CO sensing
model
Temperature
(normal operating):
+32°F to +100°F (0°C to +38°C)
Mechanical Properties
Color: White
Dimensions (diameter x H): 6.75 in. x 2.25 in.
(17.1 cm x 6.4 cm)
Power Requirements
Current (alarm):
(detector head only)
20 mA minimum at 8.5 VDC;
35 mA maximum at 32 VDC
Current (start-Up): 0.12 mA maximum at 32 VDC
Maximum RMS Ripple: 25% of DC input
Power-up Time: 22 seconds maximum
Voltage (standby)
F220-B6: 8.5 VDC to 32.0 VDC
F220-B6C/-B6R/-B6E: 10.0 VDC to 30.0 VDC
F220-B6RS: 16.0 VDC to 30.0 VDC
F220-B6PM: with D299: 18.9 VDC to 28.0 VDC
without D299: 9.6 VDC to 28.0 VDC
F220- B6PS: 18.9 VDC to 28.0 VDC
Trademarks
All hardware and software product names used in this
document are likely to be registered trademarks and
must be treated accordingly.
Ordering information
F220‑PTHC Photoelectric Smoke Detector with +135°F
(+57°C) Heat and Carbon Monoxide Sensors
Photoelectric detector head with heat and CO sensor
augmentation only; requires base.
Order number F220-PTHC
F220‑PTH Photoelectric Smoke Detector with +135°F
(+57°C) Heat Sensor
Photoelectric detector head with heat sensor only;
requires base.
Order number F220-PTH
F220‑P Photoelectric Smoke Detector
Photoelectric detector head only; requires base.
Order number F220-P
Accessories
D275 Power Supervision Module
Line supervision device for four-wire fire detection
circuits
Order number D275
DRA‑5 Remote Annunciator (5 VDC)
Designed to provide remote annunciation of alarms for
a number of Bosch smoke and heat detectors
Order number DRA-5
DT‑2 Detector Removal Tool
Use the DT‑2 to remove, replace, or test the detector
head
Order number DT-2
F220‑B6 12/24 VDC Two‑wire Base
Standard base for two‑wire (12 VDC or 24 VDC
system) applications.
Order number F220-B6
F220‑B6R Standard 12/24 VDC Four‑wire Base
Standard base for four‑wire (12 VDC or 24 VDC)
detector systems.
Order number F220-B6R
F220‑B6RS 24 VDC Four‑wire Detector Base with Soun-
der
Four-wire detector base with sounder for use with the
F220 Series Photoelectric Smoke and Heat Detectors.
Order number F220-B6RS
F220‑B6C 12/24 VDC Four‑wire Base with Auxiliary
Form C Relay
Four‑wire base with a normally‑open (NO) alarm loop
relay and a set of auxiliary contacts (Form C).
Order number F220-B6C
F220‑B6E 12/24 VDC Four‑wire Power Supervision Base
with End‑of‑line Power Monitoring Relay
Four‑wire base with a normally‑open (NO) alarm relay
and an EOL power supervision relay.
Order number F220-B6E
F220‑B6PM 24 VDC Four‑wire Addressable Master De-
tector Base
The Master base provides an address on the FACP
data expansion circuit for its detector and up to an
additional 19 detectors. It accepts the F220
Photoelectric Smoke Detector Heads and Heat
Detector Heads.
Order number F220-B6PM
3 | F220 Photoelectric Smoke Detectors
F220‑B6PS 12/24 VDC Four‑wire Addressable Standard
Detector Base
The Standard base provides an address on the FACP
data expansion circuit for its detector. It accepts the
F220 Photoelectric Smoke Detector Heads and Heat
Detector Heads.
Order number F220-B6PS
4 | F220 Photoelectric Smoke Detectors
Represented by:
Americas: Europe, Middle East, Africa: Asia-Pacific: China: America Latina:
Bosch Security Systems, Inc.
130 Perinton Parkway
Fairport, New York, 14450, USA
Phone: +1 800 289 0096
Fax: +1 585 223 9180
[email protected]
www.boschsecurity.us
Bosch Security Systems B.V.
P.O. Box 80002
5617 BA Eindhoven, The Netherlands
Phone: + 31 40 2577 284
Fax: +31 40 2577 330
[email protected]
www.boschsecurity.com
Robert Bosch (SEA) Pte Ltd, Security
Systems
11 Bishan Street 21
Singapore 573943
Phone: +65 6571 2808
Fax: +65 6571 2699
[email protected]
www.boschsecurity.asia
Bosch (Shanghai) Security Systems Ltd.
201 Building, No. 333 Fuquan Road
North IBP
Changning District, Shanghai
200335 China
Phone +86 21 22181111
Fax: +86 21 22182398
www.boschsecurity.com.cn
Robert Bosch Ltda Security Systems Division
Via Anhanguera, Km 98
CEP 13065-900
Campinas, Sao Paulo, Brazil
Phone: +55 19 2103 2860
Fax: +55 19 2103 2862
[email protected]
www.boschsecurity.com
© Bosch Security Systems 2013 | Data subject to change without notice
2701164683 | en, V3, 19. Dec 2013

Other manuals for F220

2

This manual suits for next models

3

Other Bosch Smoke Alarm manuals

Bosch Smart Home Twinguard Dimensions

Bosch

Bosch Smart Home Twinguard Dimensions

Bosch AVENAR 4000 FAP-425-O User manual

Bosch

Bosch AVENAR 4000 FAP-425-O User manual

Bosch FMM‑325A Series User manual

Bosch

Bosch FMM‑325A Series User manual

Bosch FERION 1000 O User manual

Bosch

Bosch FERION 1000 O User manual

Bosch FPD-7024 User manual

Bosch

Bosch FPD-7024 User manual

Bosch FAS-420-TM User manual

Bosch

Bosch FAS-420-TM User manual

Bosch D296/D297 User guide

Bosch

Bosch D296/D297 User guide

Bosch FAD-325-V2F User manual

Bosch

Bosch FAD-325-V2F User manual

Bosch D296 Series User guide

Bosch

Bosch D296 Series User guide

Bosch twinguard User manual

Bosch

Bosch twinguard User manual

Bosch DRA 12/24 User manual

Bosch

Bosch DRA 12/24 User manual

Bosch F220 User manual

Bosch

Bosch F220 User manual

Bosch D7050 User manual

Bosch

Bosch D7050 User manual

Bosch D340 User manual

Bosch

Bosch D340 User manual

Bosch FERION 3000 O User manual

Bosch

Bosch FERION 3000 O User manual

Bosch FERION 4000 O User manual

Bosch

Bosch FERION 4000 O User manual

Bosch FMM‑462 Series Technical manual

Bosch

Bosch FMM‑462 Series Technical manual

Bosch RADION RFSM-A User manual

Bosch

Bosch RADION RFSM-A User manual

Bosch FCD-350 User manual

Bosch

Bosch FCD-350 User manual

Bosch FAS-420-TM-R User manual

Bosch

Bosch FAS-420-TM-R User manual

Bosch RF280E Series User manual

Bosch

Bosch RF280E Series User manual

Bosch F220 B6 User manual

Bosch

Bosch F220 B6 User manual

Bosch D278S User manual

Bosch

Bosch D278S User manual

Bosch ISW-EN1242 User manual

Bosch

Bosch ISW-EN1242 User manual

Popular Smoke Alarm manuals by other brands

Comelit 48BFC000 manual

Comelit

Comelit 48BFC000 manual

System Sensor 6500RE Installation and maintenance instructions

System Sensor

System Sensor 6500RE Installation and maintenance instructions

Lexing LX728-V1 instructions

Lexing

Lexing LX728-V1 instructions

AJAX FireProtect user manual

AJAX

AJAX FireProtect user manual

System Sensor 1400 Installation and maintenance instructions

System Sensor

System Sensor 1400 Installation and maintenance instructions

Kidde p9040CA manual

Kidde

Kidde p9040CA manual

Universal MI3050S instructions

Universal

Universal MI3050S instructions

CAPIDI CAP388B user manual

CAPIDI

CAPIDI CAP388B user manual

Aico New 160 Series 160 Series Product guide

Aico

Aico New 160 Series 160 Series Product guide

UniPOS FD8040 instruction manual

UniPOS

UniPOS FD8040 instruction manual

System Sensor 2112/24S Installation and maintenance instructions

System Sensor

System Sensor 2112/24S Installation and maintenance instructions

Klaxon Battery Operated Stand Alone Fire Alarms... installation instructions

Klaxon

Klaxon Battery Operated Stand Alone Fire Alarms... installation instructions

Universal Security Instruments 3304 instructions

Universal Security Instruments

Universal Security Instruments 3304 instructions

DMP Electronics 1168 Installation and programming guide

DMP Electronics

DMP Electronics 1168 Installation and programming guide

Evolution EVC-H instruction manual

Evolution

Evolution EVC-H instruction manual

Kidde 10Y29 user guide

Kidde

Kidde 10Y29 user guide

Masterbuilt 20050106 Use manual

Masterbuilt

Masterbuilt 20050106 Use manual

Honeywell GasAlertMicro 5 user manual

Honeywell

Honeywell GasAlertMicro 5 user manual

manuals.online logo
manuals.online logoBrands
  • About & Mission
  • Contact us
  • Privacy Policy
  • Terms and Conditions

Copyright 2025 Manuals.Online. All Rights Reserved.